The cable must have a wire gauge sufficient to the amperage of the subpanel—a 100-amp subpanel requires #4 copper wires or, more commonly, #2 aluminum wires, for example.

What size copper wire do I need for 100 amp service?

SERVICE ENTRANCE CONDUCTORS SIZE AND RATING Service or Feeder Rating Copper Conductors Aluminum or Copper-Clad Aluminum 100 Amps #4 AWG #2 AWG 125 Amps #2 AWG #1/0 AWG 150 Amps #1 AWG #2/0 AWG

What wire size do I need to go 100 feet for a 100 amp service to a workshop?

For a 100 ampere circuit, the conductors will likely be required to be 3 AWG copper or 1 AWG aluminum .

Can I run a 100 amp sub panel off 200 amp main?

Yes , a 100 amp breaker can be placed in a 200 amp panel. The highest amperage allowed is the rating of the panel. If you want, you can use a smaller breaker and smaller amperage.

Will #2 wire fit in a 100 amp breaker?

#2 romex would only be good for 95 amps . If protected with a 100 amp breaker be prepared to show load calcs that load is 95 amps or less.

Can you run a 100 amp sub panel off a 100 amp main panel?

To the best of my understanding, there is no code issue running a 100A subpanel off a 100A main panel, so long as the wire size is correct, and the installation is correct. For a subpanel, you need four wire service (two hots, a neutral, and an equipment ground).

Can a 60 amp breaker feed a 100 amp sub panel?

You can feed a 100 Amp panel with a 60 Amp breaker. Keep in mind that the sub panel needs to be rated above the breaker size .

What wire size do I need to go 100 feet for a 60 amp service to a workshop?

If the circuit is 100 amp or less you have to size the conductors based on the 60-degree celsius column unless the breaker and the equipment terminations are rated for 75 or 90 degrees. You have to use a #4 conductor to feed a 60 amp circuit.

What size wire do I need to run a 100 amp service 200 feet?

If you’re trying to determine the right size wire for your 100-amp sub panel that is 200 feet away, 1-gauge wire is your best bet.

Can you run 220 on 100 amps?

You’ll be fine . Like was said above, double check the wiring leading to the sub panel, make sure the [house] breaker feeding that sub-panel is sized right for the wiring.

Can you use a 100 amp breaker for a 125 amp sub panel?

Even if not, you can order a 125A main panel and swap the main breaker to 100A. See if you can upgrade the main-sub cable to 125A. If so, order a main panel with thru lugs, which will save 2 breaker spaces, and a 125A sub. Voila, no breakers needed , space maximized!

How many circuits can be on a 100 amp panel?

Typical 100-amp panels have 20 circuits , meaning they can handle 20 full-sized breakers. 20/24 panels can hold 16 full-sized and 4 twin breakers (24 circuits in total). The number of breakers can max out to 30-42, too, depending on the design of your 100-amp pane.

What size breaker do I need for a 100 amp sub panel?

You can use the 100 amp panel off a 60 amp breaker if you determine that it is adequate, but I would suggest that in sizing your feeder wires and conduit it would be a good idea to size them to accomodate 100 amps.

Will 1 0 aluminum wire fit in a 100 amp breaker?

No, Al # 1/0 is good for a maximum of 125A in a dwelling service; possibly 100A if the distance is longer than 100′ or so. A 200A service requires a minimum of #4/0 aluminum or #2/0 copper; upsized accordingly if there is a long distance involved.

What is a 2 pole 100 amp breaker?

The Square DTM by Schneider Electric® HomelineTM 100-Amp 2-Pole Circuit Breaker is used for overload and short-circuits protection of your electrical system . This breaker is compatible with HomelineTM load centers and CSED devices. ... HomelineTM circuit breakers are the best in class.

How many amps will 2 gauge wire handle?

Wire Size 60°C (140°F) AWG (mm2) Copper 3 (26.7) 85 2 (33.6) 95 1 (42.4) 110